First time here? Check our help page!
0

Zone sensible and latend load

How can I view the sensible and latent load of each thermal zone in OpenStudio?

I am still looking for a report similar to system check sums in Trace700 but I can not find it in Openstudio.

obuchely's avatar
1.4k
obuchely
asked 2024-06-17 11:40:41 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-06-18 10:32:28 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

If for instance you're after internal "latent loads" (see here), you can request an annual tally :

image description

... and look up the results (in J) in the ESO file. You can do the same for infiltration latent loads, as well as sensible (and/or total) loads, and so on.

I think generating a concise table (in OpenStudio) from selected latent + sensible load components would require an EnergyPlus measure or customizing the OpenStudio Results Measure.