Optimum Start for VRF

Is there a way to apply optimum start to an OpenStudio building model with VRF?

I've used the air loop availability manager for Optimum Start for other HVAC systems, but I'm wondering if there's a way to model it on a VRF system specifically

apdavis's avatar
33
apdavis
asked 2023-09-08 13:05:37 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-09-08 18:51:10 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

ZoneHVAC:TerminalUnit:VariableRefrigerantFlow has an Availability Manager List Name

But the field is not wrapped in the OpenStudio SDK. So you'll need to use an EnergyPlusMeasure.

You could go upvote the feature request too if that's important to you: https://github.com/NREL/OpenStudio/is...