I have a question regarding an error that I keep getting in energypro 9

In EP 9, I am running a title 24 performance calc and when I run it, I get the error as seen below:

Error: Construction assembly 'R-19 Wall6' may not be assigned to surfaces with more than one Status, i.e. New, Altered or Existing evaluating run u rule: Set CHECKCODE ConsAssm:Status (20:'ConstructAssembly.rule' line 3332)

I just need some help understanding what this means. Thank you guys for your time and energy

Mariano's avatar
1
Mariano
asked 2023-08-23 17:47:56 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-08-25 15:37:24 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

This means that you have that Assembly (R-19 Wall6) assigned to exterior wall surfaces that are both new and altered. Create separate Constructions for Altered and Existing walls and assign them accordingly (even if they're identical to the New walls).