Severe error for ASHP with switchover control with OAT

Received the following error message. See screenshot. See energy model here.

muhl's avatar
153
muhl
asked 2023-01-20 10:05:31 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-01-24 09:05:16 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

This is one of the weird occasions where EnergyPlus reports a "severe" error, but it still allows the simulation to proceed. Note that you do obtain results in BEopt. In most cases, a "severe" error causes EnergyPlus not to proceed with the simulation in order to avoid producing erroneous results. In this case, the error seems reasonable to ignore -- it should only result in a slightly different initial temperature for the unconditioned basement, which is unlikely to lead to much of a difference in simulation results compared to if EnergyPlus had converged successfully.

It's possible that BEopt 2.8 was suppressing this EnergyPlus error and BEopt 3 is not anymore; we'll have to take a deeper look.

shorowit's avatar
11.8k
shorowit
answered 2023-01-23 11:39:14 -0500
edit flag offensive 0 remove flag delete link

Comments

Here is a bugfix version that fixes it. You can install it on top of your existing BEopt v3 beta release, no need to uninstall first.