Title 24 EnergyPro Zoning

I'm working on a Title 24 compliance model in EnergyPro for a 5-story multifamily building and I'm wondering what level of detail I need to include when it comes to zoning - is apartment-level zoning okay or do I need to distinguish individual rooms within each apartment?

Srecko Curkovic's avatar
51
Srecko Curkovic
asked 2023-01-04 16:27:33 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-01-18 14:03:53 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

2

In General, apartment level should be fine, in fact, groups of apartments subject to the same interior and exterior conditions (e.g. all dwelling units with similar orientations on the same floor) should also be fine (and save lots of set up and processing time). Check out the ACM reference manual more details on exactly what is required: https://www.energy.ca.gov/publication....

willyJohan's avatar
1.5k
willyJohan
answered 2023-01-05 17:49:56 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

In support of the previous answer, grouping zones by similarities, occupancies and/or orientation is a customary practice and is a suggested approach to keep model complexity (and subsequent runtimes) as low as possible.
A useful means of thinking about zoning may be to identify the major energy consuming components of the design to make sure they are adequately reported and tested against the Standard and zone accordingly. In the case of High-rise res, lighting is not a factor within the residential occupancy (only non-res spaces like lobbies, corridors, etc. are tested) leaving Envelope, DHW and HVAC.

Skipping Env and DHW for now.

Knowing that CBECC-Com is very granular in the testing of fan power and load right-sizing, grouping zones by System/Load (as noted in a previous answer) is a good means of maximizing what credit the simulations will offer you (especially knowing there will be little lighting credit to assist in compliance in the case of res projects).

Example: Corner Suites with multiple wall orientations (and glazing) would be modeled separately from those Apts with only one wall orientation only to be further broken down and zoned by the size of the HVAC Unit.