5

autosizing vs hardsizing HVAC system, which one is better choice?

I was wondering, what is the best way to model HVAC equipment for an already existing building? Is it better to select autosizing and let EnergyPlus to do the job OR entering all the data from manufacturers' manuals? Hardsizing will also include getting the coefficients for boilers, VRF system, heat recovery elements etc.

If Autosizing and using default equations/coefficients is the answer then will it make calibration a challenging task to perform?

Waseem's avatar
2.5k
Waseem
asked 2015-06-15 12:34:26 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2022-10-20 15:55:42 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

In the case you describe - modeling an existing building - you should use the actual equipment sizes whenever they are available as that will certainly make the model more representative of the building.

Regarding calibration, that is always challenging for the simple reason that there are a huge number of simulation inputs and usually you are comparing your simulation outputs to a very limited set of measured data. Typically only monthly (or maybe hourly) whole building energy consumption is available, without any sub-metered energy data, or zone temperature data, etc. Or in other words, it is an under-determined problem. This means that there are many potential models that will give you a match to the measured data within the error limits recommended by ASHRAE Guideline 14 and/or the IPMVP, not just one final calibrated model.

praftery's avatar
96
praftery
answered 2015-06-16 13:30:17 -0500
edit flag offensive 0 remove flag delete link

Comments

@praftery: Thanks for your answer. I got a similar reply from EnergyPlus support group few hours ago but thanks for providing answer as well. :)

Waseem's avatar Waseem (2015-06-16 15:06:21 -0500) edit