5

Fan Power Inputs in OpenStudio

Hey all. Is there a way to input fan BHP, kW, or kW/CFM in OpenStudio/energyplus? When trying to update a Packaged Rooftop VAV supply fan through OpenStudio the only fields i'm seeing are Fan Efficiency, Pressure Rise, and Motor Efficiency.

With Appendix G requiring us to calculate the total fan system kW it seems strange that OS/E+ wouldn't have an input to accept this value. Am I missing something?

Thanks, JO

anonymous user
asked 2014-10-28 13:56:50 -0500
MatthewSteen's avatar
10.1k
MatthewSteen
updated 2014-10-28 20:39:23 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

5 Answers

7

IDL-Boise has created this spreadsheet tool that will calculate fan power given a few input parameters. It will aid you in determining Appendix G requirements and E+ inputs.

Lincoln's avatar
1.5k
Lincoln
answered 2014-10-28 15:02:02 -0500
MatthewSteen's avatar
10.1k
MatthewSteen
updated 2022-04-21 16:06:17 -0500
edit flag offensive 0 remove flag delete link

Comments

Looks like a great resource, thanks @Lincoln.

MatthewSteen's avatar MatthewSteen (2014-10-28 15:18:52 -0500) edit

Thanks for sharing this tool. Looks like just what I need. JO

anonymous user Anonymous (2014-10-28 15:20:58 -0500) edit

Please reload the spread sheet . It doesn't work now.

Lee Gyoung's avatar Lee Gyoung (2021-09-22 07:31:38 -0500) edit
2

Here is an updated link to the spread sheet on our website: http://idlboise.com/content/energyplu...

DA_IDL's avatar DA_IDL (2022-04-21 15:10:50 -0500) edit
add a comment see more comments
5

No, EnergyPlus doesn't use these as inputs, instead it calculates W and W/cfm from the fan efficiency, design air flow rate, and pressure rise (see Fan section of eplustbl CSV or HTM file for fan power outputs). Because of this it requires some reverse engineering to predict what the fan power output will be from EnergyPlus.

For an Appendix G Baseline system I use USGBC's "Revised Section 1 4 Tables" XLS along with some fundamental power equations to solve for the required pressure rise to exactly match the allowed fan power. For an Appendix G Proposed system I use the data from the HVAC designer's schedule to calculate the fan power and then solve for the pressure rise. If fan BHP is given you can calculate the fan efficiency and if it's not I use the default from OpenStudio to calculate the pressure rise. This method for the proposed fan power will not predict the fan power exactly like the baseline method will, but it's close.

MatthewSteen's avatar
10.1k
MatthewSteen
answered 2014-10-28 15:05:23 -0500, updated 2014-10-28 18:16:33 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
2

You are not missing something. The fan BHP has to be done as an external calculation. PNL has documented their assumptions in the technical support documents which support the ASHRAE design guides. Refer to section 4.3.7 in the linked pdf.

Kyle Benne's avatar
6k
Kyle Benne
answered 2014-10-28 15:00:00 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

Seven years later we have the FanSystemModel and if you specify the designPowerSizingMethodto PowerPerFlowyou can specify fan power in terms of W/cfm.

Luis Lara's avatar
2.1k
Luis Lara
answered 2022-04-21 19:32:40 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

Entering the pressure rise through the fan, airflow and fan/motor efficiency will calculate the fan kW for you. I doubt that's the answer you are looking for, though.

Benjamin's avatar
1.1k
Benjamin
answered 2014-10-28 14:53:09 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments