Dehumidification (cool reheat) with chilled water (E+)

I have never modeled a chilled water air handler system that uses the cool reheat strategy for dehumidification. I've tried a few approaches that are not controlling zone humidity. I've also looked for an example file which demonstrates that capability (and did not find one) What is needed to make that happen?

Jim Dirkes's avatar
3.5k
Jim Dirkes
asked 2022-09-14 20:10:41 -0500
shorowit's avatar
11.8k
shorowit
updated 2022-09-21 23:21:18 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

This answer is a little old and OpenStudio-oriented, but I don't think any of the core info has changed.

A search of the example files folder for 'TemperatureAndHumidityRatio' returns a number of files with that input in the Controller:WaterCoil object, e.g.: 5ZoneWaterCooled_HighRHControl.idf, 5ZoneWaterCooled_MultizoneAverageRHControl.idf, 5ZoneWatercooled_MultizoneMinMaxRHControl.idf, to name a few.

ericringold's avatar
10.6k
ericringold
answered 2022-09-15 15:56:45 -0500, updated 2022-09-15 16:19:51 -0500
edit flag offensive 0 remove flag delete link

Comments

Spot on (for the controller and the example file). Thanks very much.