I get this recurring error when I run my model. what could be the reason and how do I correct it?

CalcDoe2DXCoil: Coil:Cooling:DX:SingleSpeed="POINT_OF_SALE SZ-CAV COOLING COIL" - Air volume flow rate per watt of rated total cooling capacity is out of range error continues...
*************  **   ~~~   **   This error occurred 290355 total times;
*************  **   ~~~   **   during Warmup 0 times;
*************  **   ~~~   **   during Sizing 0 times.
*************  **   ~~~   **   Max=1.116266E-004  Min=1.056579E-004

thank you,

ShaymaaSK's avatar
31
ShaymaaSK
asked 2022-05-23 13:25:40 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2022-05-23 13:39:20 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

That warning means the DX cooling coil has an air volume flow rate about 2 times higher than expected.

The volume to capacity ratio for DX coils is DX coil volume air flow/DX coil cooling capacity.

The expected range is around 0.00004 - 0.00006 m3/s/W.

The coil air flow is too high or the coil capacity is too low.

rraustad's avatar
13.8k
rraustad
answered 2022-05-23 13:36:51 -0500, updated 2022-05-23 13:37:16 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you so much for the clarification. How do you recommend I can correct the flow rate?

ShaymaaSK's avatar ShaymaaSK (2022-05-23 20:13:43 -0500) edit

Increase the cooling capacity or decrease the air flow rate by 2x.

rraustad's avatar rraustad (2022-05-31 06:08:47 -0500) edit