How can I change the air distribution effectiveness number in openstudio?

Where can I change the air distribution effectiveness number in openstudio? I want Ez to be 0.8 during heating and 1 during cooling how can I do that?

Rwadhwa910's avatar
383
Rwadhwa910
asked 2021-12-20 15:00:02 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2022-02-18 17:06:02 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

On the thermal zones tab you can choose the cooling and heating sizing parameters subtabs. There you will find the Design Zone Air Distribution Effectiveness either for cooling or heating. See also the attached picture. In the translation you will create a DesignSpecification:ZoneAirDistribution object

Petros Dalavouras's avatar
469
Petros Dalavouras
answered 2021-12-22 07:00:18 -0500, updated 2021-12-22 08:32:26 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks I found it.

Rwadhwa910's avatar Rwadhwa910 (2021-12-22 09:33:07 -0500) edit