1

fan power input in openstudio

Hey all. Is there a way to input fan BHP, kW, or kW/CFM in OpenStudio/energyplus? When trying to update a Packaged Rooftop VAV supply fan through OpenStudio the only fields i'm seeing are Fan Efficiency, Pressure Rise, and Motor Efficiency.

how can i solve this problem

Lee Gyoung's avatar
51
Lee Gyoung
asked 2021-09-22 07:23:15 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2022-02-21 20:48:10 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

1

If you use the Fan:SystemModel object, which is supposed to replace many of the other EnergyPlus fan objects in the future, you can set the Sizing Method to "PowerPerFlow" and then enter the Power per Flow Rate in units of W/m^3.

shorowit's avatar
11.8k
shorowit
answered 2021-09-22 10:39:29 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

I think you can not input directly fan BHP, kW or kW/cfm.

Check this post:

link text

obuchely's avatar
1.4k
obuchely
answered 2021-09-22 08:31:14 -0500
edit flag offensive 0 remove flag delete link

Comments

It cannnot open the spreadsheat. that is main problem

Lee Gyoung's avatar Lee Gyoung (2021-09-22 08:32:33 -0500) edit
add a comment see more comments