Does elevator contributes to the heat gains in the building

I am running a DOE prototype building for the medium office and the Elevator is consuming close to 48000 kwh, Now how can I see if that energy is contributing to the heaimage descriptionting load in the building?

Rwadhwa910's avatar
383
Rwadhwa910
asked 2021-08-02 16:14:31 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

5

The ElectricEquipment object has a field for Fraction Lost. This is the fraction of the design level (W) heat that is "lost" (i.e. fraction that is not contributing to zone heating/cooling load). If this field is zero (which it is in medium office prototype), then all heat from this equipment is contributing to the zone heating/cooling load.

image description

ericmartinpe's avatar
2.1k
ericmartinpe
answered 2021-08-02 16:53:02 -0500
Rwadhwa910's avatar
383
Rwadhwa910
updated 2021-08-03 08:35:30 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks @ericmartinpe for the answer.