Boiler Hourly Loads Energy Plus
Hi all, working on a boiler with radiant floor heat model. I have the system set to auto size the boiler and all thermal zones. I have energy bills from the building I am trying to model so know what to expect for an electricity and gas consumption as well as peak loads. When I run the model, electricity and peak loads are a good match, but my gas consumption is more than double what it should be. I spent 2 days trying to figure out the issue and I have determined that something seems off with the sizing. My peak heating load is 34 kW (116 MBH) for a design temperature of -27 C (-18 F) which is great, very reasonable. But when I look at the hourly boiler heating rate. I am getting peak loads every hour of the day from January until March, even when the outdoor air temperature is well above design day temperatures. Does anyone know how the loads are being calculated? Why are my loads so constant, they should fluctuate significantly through out the year.
Comments
I'm a little confused where you say you think the problem is sizing, but the peak load is very reasonable. Is that 34 kW the design load that is being calculated for the boiler in your EIO file? If the sizing in the EIO looks ok, then it sounds more like an operational problem. Maybe start by checking how reasonable the return/supply temps to the boiler are, making sure the loop is making setpoint and considering your boiler performance assumptions (the Curve:Biquadratic).
It may also be the case that what you see as a "peak load" is the startup load as the boiler is trying to raise the zone temp from an unoccupied setpoint to a higher occupied setpoint. This would occur only for a short time each day...
Thanks Cody, the supply and return temps to the boiler look good. After further investigation however, I think something is up with the radiant portion or the controls of my design. Supply temperatures to each radiant zone are reasonable, but a few of the zones have too high or too low of return temperatures. Also, when I check mean zone air temperature on cold days, it is dropping to well below setpoint temperature. Since I have the boiler and radiant loops set to autosize, I'm not sure why temperature isn't being maintained. I'm pretty new to Energy Plus and really appreciate the help.
Below is a link to my model if anyone has time to a look.