Shading blinds controlled by different thermal zone

I am modelling a double skin facade where I want to place solar shading inside the cavity. I am modelling it as interior blinds and I want to control them according to the zone air temperature.

But I want them to be controlled by the air temperature inside an occupied zone and therefore not in the thermal zone that the blinds are placed inside (cavity)

Is it possible to specify which thermal zone the blinds should be controlled according to?

Thanks.

juul104's avatar
63
juul104
asked 2021-03-03 02:07:11 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2021-04-07 13:13:49 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

For sure through EMS.

You have to find the right actuator (related to shading system control) and the sensor you want (the room temperature). Then you have to write ruling equations into program and you have to call it at right time into simulation timestamp.

To do it inside designbuilder it needs to have the relative module licensed