First time here? Check our help page!
1

How to represent fans for external air intake in openstudio?

Hi. I am doing the simulation for LEED ID + C v.4 certification for an office building. The air conditioning system of my project is of the VRF type. Centrifugal fans will be installed for external air supply. My question is how to represent these fans in Openstudio, to consider this external air intake?

Thank you!

Nathalia's avatar
281
Nathalia
asked 2020-12-21 07:34:00 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2020-12-21 09:23:58 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

Have you looked at the VRF with DOAS measure in BCL? Working with VRF also typically requires a separate air loop that handles outside air only (DOAS). That loop typically has cooling and heating coils in addition to a fan. Providing outside air typically requires heating and cooling, but I suppose if you must, you could just keep the fan and delete the coils. In general, I think if you search this forum for VRF, you‘ll find what you need.

mattkoch's avatar
1.1k
mattkoch
answered 2020-12-30 09:01:08 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for the answer! I modeled it as you said, created the airloop with Outdoor Air Systems and left only the Ventilation Fan, but I was in doubt if this was correct.

alt text

Nathalia's avatar Nathalia (2021-01-22 07:52:38 -0500) edit
add a comment see more comments