Is it possible to add multiple air loops to one thermal zone?

I am modeling a large manufacturing floor with about 26 package roof top units (average ~20 tons each). I have the facility floor as one thermal zone and thus would need to add 26 Package Roof top units to this one thermal zone.

However, in Open Studio, when I go to add this thermal zone to a new package roof top unit it deletes the thermal zone from the previous package rooftop unit.

My question is, is it possible to have multiple air loops feeding one thermal zone? If not, is there a different way I should thermally model the large facility floor?

Thank you,

Matt

MatthewLynch's avatar
81
MatthewLynch
asked 2015-04-16 20:01:09 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-03 19:16:01 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

4

EnergyPlus only allows one air loop per zone. Combining the units is common, although if your building is one large space, the perimeter zones may have to work harder than the core, so you may want to still make multiple zones. You can always add zone mixing objects in between the zones to add some interaction between them.

If you are conditioning with zone equipment instead of air loops, you can have multiple pieces of equipment.

David Goldwasser's avatar
20.4k
David Goldwasser
answered 2015-04-16 20:54:49 -0500, updated 2015-04-16 20:56:40 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you David,

I had a follow up question: by 'combining the units' you mean representing multiple package rooftop units as one. Thus, in this case, a 'single cooling coil DX' unit would represent 26 package units?

I will most likely go the route of creating many zones because of the size of the space, but I wanted to clarify the above point for my understanding.

If I were to condition the thermal zone with zone equipment, it seems that my only option would be multiple PTAC/PTHP units but those would not represent my 20 ton RTU's well. Would I be wrong in saying that?

Thank you!

MatthewLynch's avatar MatthewLynch (2015-04-17 09:33:44 -0500) edit
add a comment see more comments
1

If all the equipment will divide the load, I think you can model all the units as only one unit with the same performance characteristics of the each unit.