1

ChillerHeaterPerformance:Electric:EIR Object In E+?

Hello All,

Could I use ChillerHeaterPerformance:Electric:EIR Object in energyplus as an Air to water Heatpump?

Thank you

sergerwehbe's avatar
233
sergerwehbe
asked 2020-06-15 13:08:59 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-06-15 14:22:43 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

No. The ChillerHeaterPerformance:Electric:EIR object is meant to define one chiller-heater module within a Central Heat Pump System. This central heat pump system is able to then provide cooling and heating either individually or simultaneously, but it is only set up to reject heat to water and not air.

If you want to model an air to water heat pump (useful heating/cooling of water by rejecting heat to air), I would recommend using the plant loop heat pump object (one for heating and one for cooling) that allows you to select air-cooled or water-cooled condenser. This feature was added to EnergyPlus in version 9.3.

Aaron Boranian's avatar
14.1k
Aaron Boranian
answered 2020-06-15 17:44:09 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you,

In the Input output Reference (E+ 9.3): ChillerHeaterPerformance:Electric:EIR has water-cooled as the only valid condenser type!! But in E+, the ChillerHeaterPerformance:Electric:EIR object condenser could be water-cooled or air-cooled (E+ 9.3)?

For the centralHeatPumpSystem, the source loop inlet and outlet node name: what should be filled if I have an air condenser (evaporator)??

sergerwehbe's avatar sergerwehbe (2020-06-16 02:05:47 -0500) edit

Yes, the chiller heater performance and central heat pump system will only allow water-cooled condensers. That is why I recommended a different object type for an air-cooled condenser that heats/cools water - the plant loop heat pump object.

Aaron Boranian's avatar Aaron Boranian (2020-06-16 09:27:11 -0500) edit
add a comment see more comments