Compressor power of Cooling Coil

Hello everyone, I hope you are all in good health.

I wanted to present the ouput: compressor's power of a single speed dx and of multi-speed dx- cooling coil , is that possible separately other than whole coil electricity ?

Thanks!

Aly ElHefny's avatar
482
Aly ElHefny
asked 2020-06-09 11:15:03 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-06-09 12:48:30 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Preface: this is assuming that you're using EnergyPlus or one of it's interfaces.

The cooling COP input field for both single-speed and multi-speed coils account for electricity use of both the compressor and condenser fan. EnergyPlus already generates an output variable for Cooling Coil Electric Power that is the electricity use of both the compressor and condenser fan. So, you could modify the COP input to remove the electricity use of the condenser fan so that the output variable only accounts for the electricity use of the compressor. However, to do this accurately, you should also update the three performance curves related to changes in COP over the simulation:

Aaron Boranian's avatar
14.1k
Aaron Boranian
answered 2020-06-09 15:14:26 -0500, updated 2020-06-09 15:15:15 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks a lot ..

Aly ElHefny's avatar Aly ElHefny (2020-06-09 15:18:09 -0500) edit
add a comment see more comments