heating and cooling set-point for air loop supply node

I am designing a multi-zone AirLoop system that provides cooling and heating during the year. In zone:sizing,coil:heating:water, and coil:cooling:water objects I defined design supply temperature. When it came to simulation inputs I got confused.

I don't know how to specify the supply air temperature for cooling and heating season. Is it possible to define two setpointmanager:scheduled in a same node for cooling/heating modes? thank you in advance for your help.

Babak's avatar
107
Babak
asked 2020-05-30 14:34:19 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-06-01 08:34:24 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

3

I use OS:SetpointManager:OutdoorAirReset to change the set point from winter to summer.

TheEnergyTutor's avatar
868
TheEnergyTutor
answered 2020-06-01 11:46:17 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
2

You may want to put only one setpointmanager:scehduled on the supply side outled air node, therefore to modify the scheduled value in it (seasonally variyng)!

Ag's avatar
1.4k
Ag
answered 2020-06-01 03:01:41 -0500, updated 2020-06-01 14:06:52 -0500
edit flag offensive 0 remove flag delete link

Comments

@Ag That's a good solution. The problem is that there is no specific schedule for heating or cooling. Somedays both are required! Since it's a common situation, I thought there would be something like dual setpoints for thermal zones.

Babak's avatar Babak (2020-06-01 11:02:27 -0500) edit