Cooling load of a DOE prototype Building In EP

I am trying to obtain the exact cooling load for a DOE Prototype Building (Medium Office - idf). I want to understand the output variable used in Energy Plus which can provide me the cooling load for the building which occurred on air side loop. And I want to utilize the cooling load for sizing my HVAC equipment.

Thanks in advance.

VS's avatar
55
VS
asked 2020-05-28 05:56:12 -0500, updated 2020-05-28 10:00:41 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

I think it depends on the Airloop in your model. I don't know about OpenStudio, but using IDF file you can get ROOM load by (just an example!):

Output:Variable,*,Zone Air Terminal Sensible Heating Energy,hourly; !- HVAC Sum [J]

If you subtract it from the sensible cooling load on the cooling coils you can obtain ventilation load. Look at this for more informantion. You should use EMS if you want this variable reported every time step (here)

Mehrdad Vojdani's avatar
1.1k
Mehrdad Vojdani
answered 2020-05-28 08:43:33 -0500