How to model DX cooling with VAV FPB boxes?

I am trying to model DX cooling system with VAV FP boxes and they are water-cooled units. I am trying to model the same but I am unable to connect the Cooling Tower to the DX cooling coils.

How can I model this system set up in Open Studio?

Thanks

Ranjani's avatar
499
Ranjani
asked 2020-04-01 00:59:51 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-04-02 11:15:11 -0500
edit flag offensive 0 remove flag close merge delete

Comments

@Ranjani are you trying to connect water from the cooling tower to the condenser side of the DX cooling coils (water-cooled DX instead of air-cooled DX)?

Aaron Boranian's avatar Aaron Boranian (2020-04-02 11:02:41 -0500) edit

Hi @Aaron Boranian yes that is correct. Is there a way to do it? Thanks

Ranjani's avatar Ranjani (2020-04-13 19:24:03 -0500) edit
add a comment see more comments

1 Answer

1

I am not sure if you can add DX directly to a VAV box in EnergyPlus, but you could add a ZoneHVAC:WaterToAirHeatPump, which I believe does what you are describing.

See this link... https://bigladdersoftware.com/epx/doc...

sspielman's avatar
251
sspielman
answered 2020-04-02 10:42:35 -0500
edit flag offensive 0 remove flag delete link

Comments

If you want it to mimic a VAV box, you could set the fan power of the terminal to zero. You will have to be careful though, because to meet the cooling load in some zones the unit will likely want to recirculate.

sspielman's avatar sspielman (2020-04-02 10:47:31 -0500) edit

@sspielman thank you will check it out

Ranjani's avatar Ranjani (2020-04-13 19:25:25 -0500) edit