Cooling systems not working

I am trying to analyze the use of a heat pump system in a cooling only scenario using energy plus. However, the interior temperatures are always greater than the outdoor temperatures. I tried running another simulation but using an ideal load system. I still get the same type of results. In urgent need of help. Thanks a lot.

Here is the link to the idf files. https://drive.google.com/open?id=1FI0...

LostIndi's avatar
31
LostIndi
asked 2019-12-11 06:31:32 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-01-15 18:21:38 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

This problem occurred because you're not attaching your HVACTemplate:Thermostat to HVACTemplate:Zone:IdealLoadsAirSystem by its input: Template Thermostat Name. I reran your ideal load system with this fixed, it started conditioning your zones in hot hours.

Yueyue_Zhou's avatar
499
Yueyue_Zhou
answered 2019-12-17 17:50:08 -0500