Thermostat Schedule Set
Hello,
I am trying to simulate a small house in the OpenStudio Template of "Midrise Apartment". I am having troubles in ascertaining how the Thermostat behaves according to the provided Temperature values and the selected schedule set. I do not know what schedule set do I need to select in order for My HVAC System to Keep on heating the thermal zone till a particular set temperature say T is reached and as soon as T is reached the HVAC turns off. When the Temperature drops to T-1 deg F the HVAC should turn on automatically. Further, is such a setting possible in OpenStudio, if so can I get a detailed documentation of the Thermostat schedule sets of OpenStudio, if Not can anyone guide me how to realize this appropriately using Energy+ as I am referring to Energy+ documentation now.
Any help will be greatly appreciated.
Thank You.
The Following Part is for my pre-latest questions on the data which the EMS program generates when the IDF is ran through Energy Plus.(@Ivan Korolija)
The Following is the link to the Excel Results File file:
The Following is the Link to the IDF file:
The following are the Latest files (@Ivan).
Latest Excel Results File:
Latest IDF File:
Comments
Could you please elaborate further the type of HVAC system. Zone thermostats often control certain parameters of HVAC system as well (for example dumper position in VAV system, or flow rates through reheating coils) in order to maintain desired setpoint by modulating system capacity. However, if you have a system with a constant capacity (such as electric baseboard heater) you might end up with having a lot of cycling (on/off operation). I got a feeling that you would like to have a cycling system with a thermostat deadband of 1C. This might be done in EMS (and it shouldn't be complex).
I am unable to understand the Temperature 25, Temperature 18 mentioned in the "Schedule Type Limits Name" in the OpenStudio Inspector of SketchUp. I want to set the Lower and Upper bounds of Temperature for the Thermostat which will Turn the HVAC on/ off in a Heating Scenario. Also I do not need a dual set point for the Thermostat, i.e When set to heating the HVAC System will only turn on when the lower limit for Zone air Temperature is reached and will not start cooling when the higher limit of zone Air temperature is reached. I am using a PTHP system for my HVAC.
I'm not that familiar with OpenStudio, however I can guess that Temperature 25 and Temperature 18 are cooling and heating setpoints in a dual setpoint thermostat. PTHP operates in the following way: From the zone balance calculation heating (or cooling) demand is calculated to met setpoint temperature. If heating (or cooling) is required, the PTHP starts cycling heating (or cooling) coil. Since PTHP cycles coil on and off to meet the load, the coil is actually operated for a fraction of a timestep. Someone should correct me if I'm wrong. However, your desired control doesn't fit this logic...
...I'm not aware there is a thermostat control in E+ which supports your desired PTHP operation. However, you might be able to create your control by using EMS. Cooling can be excluded by setting the DX coil availability to 0 all the time so this isn't an issue. However, you'll have to play with fan and heating coil availability by switching it on and off based on your desired temperature differences. For example, you can set up heating setpoint to 21C. As soon as your zone temp. reaches 21C you can overwrite availability schedule by EMS and keep it off until zone temp. drops to below 20.
Hello Ivan,
Thank you for your comments, but I am afraid I have a few more questions. First: if I am using Packaged Rooftop Air Conditioner with an electric heating coil and a closed Air circuit, i.e. no External Air Supply and exhaust plenum, will the working be different than that of PTHP? Secondly, When I see the data of the heating energy supplied by the HVAC system, I never see them shutting off, I have 12 time steps in an hour which means 5 mins time step, and the system does not shut off at any point the whole day, which is abnormal. What is driving these performance characteristics?