Do you know why my new finished basement foundation wall option is not saving?

image description

I installed 4" xps outside of the existing brick and field-stone foundation to 8" below the level of the new slab and an error was generated as i attempted to provide such an option. (The continuous exterior isocyanurate extends to the bottom of the first floor assembly).

the basement also has 2" xps below the slab but my slab option when away when i changed to finished basement.

Moreover, why is it asking for ceiling joist spacing in the foundation wall option manager?

Thank you so much for all of this software!!!

skrucial's avatar
31
skrucial
asked 2019-09-07 20:03:22 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2022-08-12 10:43:52 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

3 Answers

2

I can reproduce the issue, it's a bug in BEopt that only seems to affect this category.

Unfortunately there is no easy way to workaround the issue -- the best advice is to pick the closest option (or do two multiple runs with different options and interpolate/extrapolate).

(The ceiling joist height is an input used in conjunction with the rim joist insulation.)

shorowit's avatar
11.8k
shorowit
answered 2019-09-10 16:13:21 -0500, updated 2020-10-26 09:22:12 -0500
edit flag offensive 0 remove flag delete link

Comments

Actually, the bug appears to affect both UCB and CB walls. I can make UCB ceiling entries just fine, but UCB walls also triggers this error. This configuration is rare, but I wanted to compare foundation wall draped FGB vs. insulated frame floor and could not.

jpierce's avatar jpierce (2022-10-24 10:38:28 -0500) edit
add a comment see more comments
1

I'm not sure why it cannot be saved, but note that Continuous Insulation Nominal R-value is total R, not R/in, so your entry should be 20 not 5. The Whole Wall R-20 XPS is probably your best bet. As for ceiling spacing values, those are so that it can calculate how much of the rim joist is thermal bridging to the floor versus exposed/insulated.

BEopt's Slab entries are for slab-on grade. Since the ground's temperature below the frost-line/in a basement is relatively constant compared to the ambient temperature, the software simplifies inputs and ignores under-slab insulation. This is a fairly reasonable simplification unless you have radiant heating in the slab, which BEopt itself does not explicitly handle anyhow.

jpierce's avatar
375
jpierce
answered 2020-10-26 09:36:48 -0500, updated 2020-10-26 09:43:09 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

I just ran into this same issue. One work around is to use BEopt 2.7, this bug doesn't seem to be present in the older version of BEopt and I was able to model a custom basement wall. You can update the BEopt 2.7 file to 2.8, but when I attempted to add the option to the library, ran into the same error message.