Heating cooling demand and district systems

I haventaven't got a clear idea of district heating and cooling. Can I consider district systems like a "machine" with an COP and EER of 1? For example, If I have this outputs and i want to use a heater of COP 0.8, Can I just multiply the District heating output with 0.8? Thank you.

gonchotorena's avatar
181
gonchotorena
asked 2019-07-18 04:54:49 -0500
shorowit's avatar
11.8k
shorowit
updated 2019-07-18 11:23:15 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Yes, the DistrictHeating and DistrictCooling objects output total energy transfer, so if you know your district systems annualized COP for heating and cooling you can multiply that by the district output to get total energy use.

mdahlhausen's avatar
9.5k
mdahlhausen
answered 2019-07-18 10:49:21 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank for your answer. All clear.