Determining heating and cooling annual and peak loads

Hi,

I am looking to determine building heating and cooling loads to size geothermal systems.

What is the most valid way to determine these loads? 1. Use "Ideal Air Loads", and then manipulating the loads with the cop and eer ratings of the ground-source-heat-pumps? 2. Use conventional HVAC, and then manipulating the loads with the cop and eer ratings of the ground-source-heat-pumps? 3. Attempt to simulate a ground source heat pump system.

mdewy's avatar
53
mdewy
asked 2019-07-04 08:27:38 -0500
shorowit's avatar
11.8k
shorowit
updated 2019-09-10 17:32:25 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

What software are you using? COP and EER do not change cooling and heating loads. They change energy consumption.