There is no heating electricity consumption in my model

Hi , everyone

I am sorry to disturbe you . When I run my model using idealHVAC , There is no heating electricity consumption in my report . Could you tell me why ? Thank you very much.

zhao chuan's avatar
23
zhao chuan
asked 2019-06-12 07:56:15 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

4

As far as I know, the IdealLoadsAirSystem didn't build a full HVAC system and assumes 100% efficiency. It won't generate heating and cooling electricity consumption, instead it would be under District Cooling and District Heating columns in your html report which accounts for load-only calculation. Hope it helps. And an idf would help to address your problem too.

Yueyue_Zhou's avatar
499
Yueyue_Zhou
answered 2019-06-12 15:47:32 -0500, updated 2019-06-12 15:48:30 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

The IdealLoadsAirSystem reports it's energy consumption as DistricHeating and DistrictCooling energy. You can see this line in the source code for the Input-Output reference shows it. For some reason, it was not correctly compiled in the BigLadder online version of the I/O reference. If you want to use electricity in your model, you can use a system that has a HeatingCoil:Electric object.