CHW Scheduled setpoint Manager

Dear All,

In one of the project, the requirement is to achieve two different CHW temps as there are two loops working on the different temps. The attached screenshot is simplified version of my problem. here i defined two SPM, one at 12 degC and another at 14 degC. When i checked .eso, the hourly report shows 12 degC for both the loops whereas SPM-2 has 14degC defined. I thought the use of heat exchanger gives us capability to have different temps at the sub-loops. Am i missing something?

Thanks,

C:\fakepath\ChillerPlantLayout_SPMIssue.jpeg

Javed's avatar
273
Javed
asked 2019-04-02 07:41:05 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2019-04-02 17:53:19 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

The problem was with the HeatExchanger:FluidToFluid control type. It got resolved finally.

thanks,

Javed's avatar
273
Javed
answered 2019-04-02 09:37:54 -0500