energyplus heating and cooling load

I'm working on FCU + DOAS system, I find that if I increase the outdoor air Volume., the load of FCU coil and DOAS coil will increase simultaneous (component sizing summary). the load has been doubled.

what shall I do if I want to use FCU deal with internal load, while use DOAS to deal with outdoor air load.

thank you

xzb86's avatar
311
xzb86
asked 2019-03-15 04:30:09 -0500
MatthewSteen's avatar
10.1k
MatthewSteen
updated 2019-03-16 21:09:51 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Do you have an outdoor air flow rate set in your fan coil units?

mdahlhausen's avatar mdahlhausen (2019-03-15 10:41:02 -0500) edit

yes, I add the OA flow rate in the HVACTemplate:Zone:FanCoil,, because I'm not sure how to add OA flow rate directly into the HVACTemplate:System:DedicatedOutdoorAir,.

xzb86's avatar xzb86 (2019-03-16 10:14:09 -0500) edit
add a comment see more comments

1 Answer

2

Set the outdoor air flow rate in your fan coil units to zero and then add a DOAS air loop with terminals serving each zone.

mdahlhausen's avatar
9.5k
mdahlhausen
answered 2019-03-16 12:35:23 -0500
edit flag offensive 0 remove flag delete link

Comments

ok, I have a DOAS terminal (AirTerminal:SingleDuct:VAV:NoReheat), but how can I set OA to this terminal? I find no OA setting in this air terminal.

xzb86's avatar xzb86 (2019-03-16 18:04:09 -0500) edit

Set the outdoor air requirement with the DesignSpecificationOutdoorAir object. Alternatively, you can use the AirTerminal:SingleDuct:Uncontrolled object and size the terminal for the outdoor air flow rate directly. Make sure the sizing criteria for the air flow is set to account for the DOAS and sized to air flow requirement.

mdahlhausen's avatar mdahlhausen (2019-03-18 10:23:57 -0500) edit