Monthly cooling coil sensible outputs.

I am trying to obtain the monthly sensible cooling coil energy for the cooling coil of type Coil:Cooling:Water. However the CoilReportMonthly is giving an output of 0 for the Cooling coil sensible cooling energy for all months, even though the cooling coil total cooling energy appears to be reported appropriately. Is this a energyplus error. I am using version 8.9.

kbk78's avatar
601
kbk78
asked 2018-12-06 16:16:23 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

This is a known issue in v8.9 and v9.0.1 (and maybe earlier). The workaround is to add Output:Variable objects for the variables matching each base column of the report. Max/min/dates will be populated once the base columns are working.