simplest HVAC system

I want to build a simplest hvac system in energy plus with constant air temperature and constant air flow rate. Is it possible? Can I use ZoneHVAC:IdealLoadsAirSystem to build it?

vibra's avatar
65
vibra
asked 2015-03-08 13:25:22 -0500
Neal Kruis's avatar
4.7k
Neal Kruis
updated 2015-03-08 16:22:55 -0500
edit flag offensive 0 remove flag close merge delete

Comments

ZoneHVAC:IdealLoadsAirSystem is the simplest HVAC system in EnergyPlus. The next simplest might be the ZoneHVAC:PackagedTerminalAirConditioner. Are you looking for a central air system that serves several zones? If the system supplies constant air volume and constant temperature, how are the temperatures of the zone controlled to a set-point? Do you need reheat coils as well?

Neal Kruis's avatar Neal Kruis (2015-03-08 16:32:58 -0500) edit

Thank you for your reply, Neal. This is my idea: when temperature is greater than 24C, Cooling start with constant T (15C) and constant flow rate. When temperature is lower than 20C, Heating start with constant T (27C) and constant flow rate.
I'm using energy+ for parameter optimization. So I hope the HVAC model could be as simple as possible.

vibra's avatar vibra (2015-03-09 11:32:39 -0500) edit

So you want a system that cycles on and off to meet the zone setpoint? Why is it important that the airflow rate and temperature are constant?

Neal Kruis's avatar Neal Kruis (2015-03-09 12:37:16 -0500) edit

Yes.I'm trying to identify the building as a black box. The HVAC system could be considered as input to the system. I need to know what exactly the value of the input is.

vibra's avatar vibra (2015-03-09 15:10:40 -0500) edit
add a comment see more comments

1 Answer

1

Your best bet would probably be ZoneHVAC:PackagedTerminalAirConditioner with a Fan:OnOff. You can use this system to provide a set flow rate and temperature for cooling and heating operation, and it will cycle on and off to meet the load in the zone.

This is more complex than ZoneHVAC:IdealLoadsAirSystem because it requires fan, heating coil, cooling coil, and outdoor air mixing objects. I suggest looking at an example file to see how this object is used if you aren't familiar yet with how it works with the other objects.

Neal Kruis's avatar
4.7k
Neal Kruis
answered 2015-03-09 15:29:20 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks. I'm looking into the example file. I also have another question. I want to change the initial condition of the simulation. (like the indoor temperature at the very beginning) But I found this from the documentation:

EnergyPlus “runs” the first day of the environment (starting with a set of hard-coded initial conditions) until the loads/temperature convergence tolerance values are satisfied or until it reaches “maximum number of warmup days.

Does it mean there is no chance I can modify the initial condition?

vibra's avatar vibra (2015-03-10 01:32:19 -0500) edit
1

@vibra this is an excellent question! You should post it as a new question so that other people with the same question can find it too.

Neal Kruis's avatar Neal Kruis (2015-03-10 10:05:47 -0500) edit