How to control the outcome of Chiller IPLV, so that it is as desired?

I have been working on expanded .idf files to fix the iplv value for chillers, but I have noticed that the values only come close to the desired iplv value and needs subsequent iterations for correction. This is a problem for cases where the simulations take a lot of real time. Is there a way to enter the correct exact coefficient that gives the desired output ?

Sid's avatar
21
Sid
asked 2018-10-12 04:49:58 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2019-02-28 05:57:39 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

I understand that iterations would be necessary to adjust results of a simulation. The chiller IPLV can be changed by adjusting the chiller performance curves. Others have done this in a spreadsheet prior to the simulation. If you are using the simulation to determine the IPLV for the current performance curves then you can minimize the time a simulation takes by performing only a design day simulation and use a 1 hour time step. The calculation of IPLV does not need an annual simulation. Use only 1 SizingPeriod:DesignDay to speed up the simulation time.

Timestep,1;

SimulationControl,
  Yes,                     !- Do Zone Sizing Calculation
  Yes,                     !- Do System Sizing Calculation
  Yes,                     !- Do Plant Sizing Calculation
  Yes,                     !- Run Simulation for Sizing Periods
  No;                      !- Run Simulation for Weather File Run Periods