Add HVAC system cause simulation terminated

Hi guys, I'm trying a single zone HVAC setting, but as I shown in the topic when assigning PTAC system. Somehow it shows the fatal issue, something like Field〔control zone name〕is required but was blank...

** Severe  ** IP: IDF line~2475 Error detected in Object=SETPOINTMANAGER:SINGLEZONE:REHEAT, name=SETPOINT MANAGER SINGLE ZONE REHEAT 3
**   ~~~   ** Field [Zone Inlet Node Name] is required but was blank
************* IDF Context for following error/warning message:
************* Note -- lines truncated at 300 characters, if necessary...
*************   2725 SetpointManager:SingleZone:Reheat,
************* indicated Name=Setpoint Manager Single Zone Reheat 4
************* Only last 5 lines before error line shown.....
*************   2726   Setpoint Manager Single Zone Reheat 4,  !- Name
*************   2727   Temperature,                            !- Control Variable
*************   2728   -99,                                    !- Minimum Supply Air Temperature {C}
*************   2729   99,                                     !- Maximum Supply Air Temperature {C}
*************   2730   ,                                       !- Control Zone Name

Attached pictures.!image description image description Hope someone could kindly help. Thanks!

borui's avatar
73
borui
asked 2018-05-29 05:28:15 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2018-05-29 07:18:51 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

1

Click on your SPM (the blue "flag" placed on the supply outlet node of your plant Loop). Make sure the "Control Zone Name" is actually filled and matches your connected zone name.

If that still doesn't work, try disconnecting and reconnecting your zone to your AirLoop

Also ensure that your thermal is actually being translated: it must have at least one space assigned, and said space must have some geometry assigned with it. You can open the resulting "in.idf" to ensure the zone does exist.

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2018-05-29 07:20:14 -0500, updated 2018-05-29 07:20:21 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

Thanks to Julien,But I check the "Control Zone Name" again and the assigned thermal zone properties seems well. Somehow couldn't launch simulation in Openstudio.

While checking the idf file, there're some items should be set but unknown, which made me confused. Controller: MechanicalVentilation setting part doesn't synchronize to the control thermal zone and several nodes input are blank as well, should that be filled in? I'm wondering where can I find these setting places in OS.

image descriptionimage description image description

Thanks for the kind help!