Unmet heating and cooling hours question

I'm experimenting with energy modeling using Openstudio through Honeybee. I modeled a building and I used the ideal air load system. I got some unmet heating and cooling hours. Shouldn't an ideal air load system yield 0 unmet heating and cooling hours considering it is ideal (energy coming in the zone = energy going out of the zone)? Am I misunderstanding something here!

Arch2010's avatar
129
Arch2010
asked 2018-05-08 14:06:43 -0500, updated 2018-05-08 22:46:56 -0500
edit flag offensive 0 remove flag close merge delete

Comments

@Arch2010 could you post a link to your model?

Avi's avatar Avi (2018-05-09 10:48:49 -0500) edit
add a comment see more comments

2 Answers

2

The ZoneHVAC:IdealLoadsAirSystem can also be used to model a real system. For "ideal" modeling make sure the inputs for Cooling Limit and Heating Limit are set to "NoLimit" and that the Cooling/Heating Availability Schedule input fields are blank (always available). If this still produces unmet hours, plot zone temp, zone set point temperature and unmet hours reports (then zoom in on a few days) to see when this is happening.

rraustad's avatar
13.8k
rraustad
answered 2018-05-09 07:32:33 -0500
edit flag offensive 0 remove flag delete link

Comments

@rraustad, I didn't know that I have to set the cooling and heating limit to no limit. Thanks!

Arch2010's avatar Arch2010 (2018-05-13 14:49:43 -0500) edit
add a comment see more comments
-1

Check the occupancy schedule versus HVAC schedule

TomB's avatar
1.7k
TomB
answered 2018-05-09 01:44:35 -0500
edit flag offensive 0 remove flag delete link