3

Space infiltration pressure values / units

Hi everyone, I'm new to OpenStudio and was trying to input an air leakage rate per exterior surface area for my model. I went to the "spaces" tab, then found "space infiltration design flow rates" and would like to insert data under "flow per exterior surface area [m/s]".

Question: Is the flow per exterior surface area input the measured value at 75Pa, or is it at some other pressure? I noticed the other items also don't have any pressure conditions so I'm a bit lost here.

Any insight would be greatly appreciated. Thanks!

Jono's avatar
305
Jono
asked 2018-03-14 14:34:31 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-03-14 18:28:42 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

I believe it is 4 Pa differential pressure but you could read about it yourself in the Input Output Reference. Also try the Engineering Reference.

Avi's avatar
4.3k
Avi
answered 2018-03-15 08:25:22 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for the info. I've read through the documents and noticed 4Pa is specified for Effective Leakage Area, but not specifically stated for the others.

Jono's avatar Jono (2018-03-15 15:01:37 -0500) edit