3

can we model both Radiant Panel and Radiant slab cooling in Energy plus?

is it possible to model the Following Systems in Energy plus?

a) Radiant Panel Cooling

b) Radiant Slab Cooling.

c) Cold storage of -10 degC

Can it be possible to model the above conditions in Design builder also?

Siva's avatar
295
Siva
asked 2018-03-04 01:38:41 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-03-05 07:29:06 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

5

a) Certainly, as you can read in the Input Output Reference.

b) Yes if you are referring to Ventilated Slab Cooling. Look here.

c) Again certainly, look here.

Avi's avatar
4.3k
Avi
answered 2018-03-04 05:12:49 -0500
edit flag offensive 0 remove flag delete link

Comments

@Avi can this be possible to model in Design Builder?

Siva's avatar Siva (2018-03-04 05:39:47 -0500) edit

@Siva I am not familiar with Design Builder but I believe it should be possible to do. By the way it is possible to do that in OpenStudio.

Avi's avatar Avi (2018-03-04 06:05:14 -0500) edit
add a comment see more comments
3

For modeling Radiant Slab Cooling refer to the following link:

http://www.beepindia.org/sites/defaul...

I hope Radiant panel can be also modeled using the same methodology.

Regarding Refrigeration you need to tweak process load as desribed in DB help:

http://www.designbuilder.co.uk/helpv5...

Do let me know if you are able to model the same.

Maaz Akbar's avatar
93
Maaz Akbar
answered 2018-03-23 08:28:20 -0500, updated 2018-03-23 13:26:31 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments