Cooling energy for HVACTemplate:System:DedicatedOutdoorAir

I want to verify the result exporting air system cooling energy from the model which implement FCU and PAU(for FA supply)
However, when I export Air System Total Cooling Energy, it seems that cooling energy by PAU is not included.
Does anyone know how I can export cooling energy for PAU?

katsuya.obara's avatar
2.1k
katsuya.obara
asked 2017-10-05 04:00:16 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

"Air System Total Cooling Energy" should give you "DOAS:Air System Total Cooling Energy [J]" which is a cooling energy by PAU (if this is DOAS). The cooling energy for FCU can be found by "Fan Coil Cooling Energy"

Piljae Im's avatar
26
Piljae Im
answered 2017-10-05 13:52:52 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you! What about the case for HVAC:System:VRF?

katsuya.obara's avatar katsuya.obara (2017-10-06 02:12:41 -0500) edit

You can use "VRF Heat Pump Total Cooling Rate"

Piljae Im's avatar Piljae Im (2017-10-06 15:21:47 -0500) edit