Hi all, PCM manufacturers often provide the following technical data on their products:

  • 'Switching' temperature 23°C
  • Latent heat capacity ∆H 330 kJ/m2 at 'switching temperature'
  • Specific heat capacity approx. 1.20 kJ/kgK
  • Thermal conductivity λ approx. 0.18 W/(mk)

How can one define the enthalpy curve of the material for the use in EnergyPlus based on this? The IDF file takes inputs as shown below. With the ∆H provided for the switching temperature I can describe the jump at 23C but how is the base enthalpy of the material inferred so that data-points for -20C, 20C and 100C can be provided to EnergyPlus.

MaterialProperty:PhaseChange,
PLASTER OR GYP BOARD, !- Name
0.0, !- Temperature coefficient ,thermal conductivity(W/m K2)
-20., !- Temperature 1, C
0.01, !- Enthalpy 1 at –20C, (J/kg)
20., !- Temperature 2, C 33400, !- Enthalpy 2, (J/kg)
20.5, !- temperature 3, C 70000, !- Enthalpy 3, (J/kg)
100., !- Temperature 4, C 137000; !- Enthalpy 4, (J/kg)

Tim's avatar
163
Tim
asked 2017-06-28 04:18:09 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-06-29 10:47:41 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Hi Tim. It is not possible to form the enthalpy-temperature curve through the thermophysical data. These curves are usually drawn using the data from experiments. Most manufacturers do not provide all details of their products. However, they provide an email address which you can contact them for more detailed enthalpy-temperature curves. Here are the links of some suppliers that can help you through.

Rubitherm GmbH

CRISTOPIA Energy Systems

Teappcm

Nima8927's avatar
11
Nima8927
answered 2017-11-18 04:42:30 -0500