1

is it possible to acheave 100% relative humidity at the outlet of an evaporative cooler by precooling the air about 2 or 3 degrees?

is it possible to acheave 100% relative humidity at the outlet of an evaporative cooler by precooling the air about 2 or 3 degrees?

amirrezaheydari's avatar
673
amirrezaheydari
asked 2017-05-17 07:51:25 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-17 12:06:18 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Even if you do not precool,you would need a 100% efficient device.

Ricardo GAllegos's avatar
274
Ricardo GAllegos
answered 2017-05-18 11:47:47 -0500
edit flag offensive 0 remove flag delete link

Comments

Dear Sir Thank you for your answer, but it is not obvious for me. Do you mean that using an evaportative pad alone, I need a 100% efficient pad, but by precooling I can achieve 100% relative humidity? Thank you

amirrezaheydari's avatar amirrezaheydari (2017-05-19 02:59:26 -0500) edit

The efficiency of an evaporative cooler is by definition ; e= (tdi - tdo) / (tdi - twi)

tdi= Dry bulb temperature at inlet

tdo = Dry Bulb tempeature at outlet

twi= Wet bulb temperaature at inlet.

The minimum outlet temperature would be twi, and at that point you have 100% saturation. But at the same time, it implies that e=1 (100%) So if you precool, you lower tdi, but only if tdo=twi you can have 100% saturation, and 100 % efficiency, which is not posible. In a pshychrometric chart, you will have two paralel lines, but none touches to the saturation curve.

Ricardo GAllegos's avatar Ricardo GAllegos (2017-05-19 13:48:32 -0500) edit