1

How to automatically size chiller equally ?

I found out that the calculated size of chiller is the same for having one chiller in the loop or two, or three or even more. Is it possible to let the OS automatically split the chiller size equally ?

Or has it to be done by hard size ? (e.g size of one chiller / number of chillers)

Thank you

BL's avatar
980
BL
asked 2017-03-21 13:31:41 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-08-07 13:22:40 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

5

The 'Sizing Factor' field in your chiller object can be used to distribute the peak load between autosized components.

image description

If you have two chillers and you would like them to be sized equally, enter '0.5' as the sizing factor for each chiller.

Lyle K's avatar
2.2k
Lyle K
answered 2017-03-21 13:50:40 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments