Sorry, this content is no longer available
2

Is possible to calculate the heating rate using COMPACT HVAC:ZONE:PURCHASED AIR in Energy Plus v. 8.6?

I'm trying to calculate the heating rate. The InputOutputReference of 2008 and others documents suggest to use the COMPACT HVAC:ZONE:PURCHASED AIR. But I'm using the version 8.6 of Energy Plus and can't find that class. There is something equivalent in the version 8.6?

melanie's avatar
333
melanie
asked 2017-02-17 23:13:37 -0500, updated 2017-02-17 23:14:12 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

Ideal Load Air System is a concept totally equivalent to purchased air. Check the input output reference manual. You can use the HVACTemplate objects for convenience:

Or the ZoneHVAC:IdealLoadsAirSystem directly.

Ricardo GAllegos's avatar
274
Ricardo GAllegos
answered 2017-02-20 15:37:30 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2017-02-21 05:36:00 -0500
edit flag offensive 0 remove flag delete link

Comments

I took the liberty of adding links to the documentation and mention the non HVACTemplate option.

Worth reading the first paragraph here:

The simplest way to add HVAC control to an EnergyPlus thermal zone is to use the ZoneHVAC:IdealLoadsAirSystem. This was called purchased air in older versions

Julien Marrec's avatar Julien Marrec (2017-02-21 05:36:21 -0500) edit