Humidity Control in Detailed HVAC

When Using the Detailed HVAC do we need to add a humidifier to the Air Handling Unit? Does the software not automatically take the humidity set points from the Activity set?

Humidity in Activity Tab

Problem is when I am changing the RH Humdification and Dehumidification set points the results are not giving any changes in energy.

Junaid Bin Masood - The Petroleum Institute's avatar
183
Junaid Bin Masood - The Petroleum Institute
asked 2017-01-30 09:20:32 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-03 20:55:49 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

It depends of the programation on Model Options. If you designate Detailed HVAC and Option 2-Detailed HVAC Data in Detailed HVAC Activity data, the (Des)Humidification setpoint used are the setpoints in HVAC Zone. Otherwise, if you designate Option 1-Simple HVAC Data in Detailed HVAC Activity data, the (Des)Humidification setpoint used are the setpoints in Activity Data. You have to model (Des)Humidification process in AHUs modeled.

I recommend you seeing this text:

https://www.designbuilder.co.uk/helpv...