Ideal Air Load V1.5.0.2

I am having some trouble getting my model to run. I decided to use just Ideal Air loads but the model gives an error that the Zone 1 (of 9), node 1 inlet node name needs to be specified. If I am not specifying equipment why would I need to specify controls? Thank you, Matt

MattStewart's avatar
565
MattStewart
asked 2014-12-30 01:21:54 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-07-12 18:12:54 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

OpenStudio uses the EnergyPlus object named HVACTemplate:Zone:IdealLoadsAirSystem, which expands into ZoneHVAC:IdealLoadsAirSystem to model ideal systems. Ultimately the ZoneHVAC:IdealLoadsAirSystem does connect to the zone via nodes, however this is managed by OpenStudio for you. All that you normally need to do is check the box to enable ideal air loads. Are you enabling ideal air loads using the interface in the screenshot? Can you provide the full error message, or perhaps even the entire model?

image description

Update

After reviewing the model I found that the failure is caused by a VAV air system that does not have any zones attached.

image description

I added a terminal and attached the two zones in the model that did not have ideal air loads turned on (zones 8 and 9) and the model did simulate. You could alternatively remove the system (and supporting plant) entirely.

image description

There are still some warnings that you might want to heed. Particularly the warning about no thermostats in the zones.

Kyle Benne's avatar
6k
Kyle Benne
answered 2014-12-30 08:50:22 -0500, updated 2014-12-30 13:55:53 -0500
edit flag offensive 0 remove flag delete link

Comments

Dear Kyle, Dear Kyle, I would be extremely grateful if you could take a look. The forum is not allowing me to attach. The last message I sent will not post for several days. Apparently I need to earn points to post with attachment. my email is matt.stewart@aec.us if you can send me a message I will be able to send the .osm file. Thank you in advance for your assistance. Best Regards, Matt

MattStewart's avatar MattStewart (2014-12-30 09:44:07 -0500) edit
1

I sent you an email.

Kyle Benne's avatar Kyle Benne (2014-12-30 13:00:06 -0500) edit

Dear Kyle, Dear Kyle, Thank you so much for your help. It looks like it will run with Zones 8&9 turned off and Zones 1-7 turned on. I have cooling and heating thermostats specified but am confused about the Setpoint Manager. This is a node on the Supply Side with a control variable and schedule that is separate. Does this control OA or adjust thermostats based on outside temperature? There are limited choices and using temperature requires a schedule name. Can you provide an example of what the schedule name might typically be. Thank you Matt

MattStewart's avatar MattStewart (2014-12-30 15:00:49 -0500) edit
add a comment see more comments