design size rated cooling vs calculated design load
Hi,
In a project, a thermal zone with a doa and a default water to air heat pump, cooling thermostat 22°C, the maximum outdoor temp is 21°C, and density correction fctor is 0.731, the resultant are:
Design Size Rated Total Cooling Capacity 53964 W
(the first)
CALCULATED DESIGN LOAD 18,117 W
If the there is no heat gain from DOA, why is the difference between results?
There is no safety factor in the project.
How can i attach a project?
Comments
Please tag with software you are using. Also, please try to avoid creating new tags. Nobody is subscribed to the tag 'vs'. Thanks.
OPEN STUDIO 1.10.0, because this version allow me to select air cooled chillers with evaporative condenser and the latest version doesn't allow this.
can you please retag?