Error detected in Object=SETPOINTMANAGER:SINGLEZONE:REHEAT

when I try to run my simulation it shows this error:

  • Severe * IP: IDF line~7378 Error detected in Object=SETPOINTMANAGER:SINGLEZONE:REHEAT, name=SETPOINT MANAGER SINGLE ZONE REHEAT 2 * ~~~ * Field [Control Zone Name] is required but was blank...

image description

I am sure that it is due to " Packaged Rooftop Air Conditioner 7" and it should be "Packaged Rooftop Air Conditioner 1" but I do not know how to do that? My file is here to download.

Thanks in advance for any guidance.

4Designer's avatar
738
4Designer
asked 2016-06-04 15:28:17 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

2

The error message means your airloop is not controlling any zones. Go back the HVAC tab and go through each airloop for insanity check.

Yijia's avatar
180
Yijia
answered 2016-06-04 16:25:50 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

@Yijia Wang,Thank you so much. As you said I checked my air loop "Packaged Rooftop Air Conditioner 1" and understood there was not zone of classroom-2, then I applied this zone for it and also I added a Diffuser from Libray(Air Terminal Single Duct Uncontrolled).Now my model works.