1

How do I use a wall fan ventilation on E+?

The building is naturally ventilated but have also electric wall fans ventilation system on the rooms. I didn't find a idf option to simulate that. Any suggestion?

Raquel's avatar
21
Raquel
asked 2016-05-23 08:27:28 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-05-23 13:13:50 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Please tag your question with the software your are using (energyplus and/or openstudio since you mention idf)

Julien Marrec's avatar Julien Marrec (2016-05-23 11:29:08 -0500) edit
add a comment see more comments

1 Answer

2

You can either use:

Both of them are available in OpenStudio and will allow you to input airflow and fan electricity consumption. The first one makes it simpler to add infiltration to compensate for exhaust for example, so I suggest starting with this one.

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2016-05-23 11:36:19 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments