How to put schedule for switching on SPLIT HVAC in Openstudio?

In my model there are 2 thermal zone swith an unitary SPLIT HVAC System each that are operated independently. In reality, these Split AC are operated manually when the building is occupied, e.g. for example in a residential building when people come home after work they switch on AC.

Now I am not sure which class to address while creating the schedule? For example, I could put the schedule for the cooling set point very high when the building is not occupied. But I was wondering if there is a cleaner solution, e.g. operational schedule of HVAC system or I saw something like Availability Manager.

Xandrika's avatar
1.1k
Xandrika
asked 2014-12-01 13:46:52 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

5

If you are modeling this with a ZoneHVAC system like a PTAC, then you could use the availability schedule.

image description

If you are modeling with an AirLoopHVAC based system, then you could use the "HVAC Operation Schedule" on the "Control" tab of the air loop interface.

image description image description

Kyle Benne's avatar
6k
Kyle Benne
answered 2014-12-01 15:18:29 -0500
edit flag offensive 0 remove flag delete link

Comments

@Kyle Benne Thanks al lot. I got it. Is there also an options for an operational/availability schedule when I am simulating with IDEAL AIR LOADS?

Xandrika's avatar Xandrika (2014-12-01 22:03:11 -0500) edit

Not in OpenStudio.

Kyle Benne's avatar Kyle Benne (2014-12-02 08:30:30 -0500) edit

what is the different bewteen the always on discrete and bldg occupancy operation schedule! is the fan will be running continuously when occupied and cycling when nobody the bldg using the setpoint temp schedule or the occ schedule !!

Bassam's avatar Bassam (2017-05-19 11:15:07 -0500) edit