Hello, My model has water to air heat pump mostly for cooling and single duct terminal units provide heating to each zone. Somehow I'm getting failure after 2hr 10 min as "CheckForRunawayTemps: Simulation terminated because of run away plant temperatures, too hot. Does anyone have a similar experience?

Thank you Elvin

elvin's avatar
161
elvin
asked 2016-04-04 09:17:04 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2021-05-07 09:53:26 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Which simulation tool are you using? Please add the tag for it in the question so others can help you better

Aaron Boranian's avatar Aaron Boranian (2016-04-04 09:23:58 -0500) edit
add a comment see more comments

1 Answer

2

Without looking at your model, it seems that there are two possibilities:

  • You do not have a bypass branch on the supply and demand side of your plant. These still allow flow to occur in the plant, but avoid components like heat pumps and coils that will exchange heat with the fluid when it's not desirable.
  • You have a pump that is operating all the time. Efficiency losses in pumps translate to some heating transferred to the fluid. Whether you're using a constant or variable speed pump, make sure that the Pump Control Type input field is set to "Intermittent" and not "Continuous".