Modeling a Standard Split AC with economizer
I followed the steps in the question "hvac template for standard split ac"to build up a standard split system according to the technical data: http://www.inventorairconditioner.com...
The only changes I made from the default are:
Unitary - Single Speed DX cooling - Cycling - Elec reheat
- OS:AirLoopHVAC:UnitarySystem
Controlling Zone or thermostat location: Τhe relevant zone
- OS:Coil:Cooling:DX:SingleSpeed
Rated Total Cooling Capacity: 6156 W
Rated COP: 3.24
- OS:Coil:Heating:Electric
Nominal Capacity: 6498 W
Diffuser
- OS:AirTerminal:SingleDuct:Uncontrolled
Maximum Air Flow Rate: 0.236 m3/s (Air Circulation 850 CMH Max)
My first question is if my settings are correct according to the technical data?
The second Question is according to openstudio results summary. Using a Unitary - Single Speed DX cooling - Cycling - Elec reheat system the total calculated power consumption for cooling or heating is cooling/heating+fans consumption?
The third question is if I can model an economizer, since the relevant zone is a IT room/Data center space and what are the appropriate settings for an economizer for such a space so as to estimate possible changes in energy consumption
Thanks!
EDIT-------------------------------------------------------------------
The following error occurs:
"Error: Sizing: Coil:Cooling:DX:SingleSpeed "1SPD DX CLG COIL 7": Rated air volume flow rate per watt of rated total cooling capacity is out of range. Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[8.196E-005], Max Rated Vol Flow Per Watt=[6.041E-005]. See Input Output Reference Manual for valid range."
When all set to default (autosize), no error occured. Acording to the technical data, is it posible to be overrided this error?