I wanted to know the quickest and most effective way to model a ceiling fan in Openstudio. The fan only displaces air in the zone and does not bring it from outdoors. If possible I would like a fan for which you can choose the air displacement (linked to the size of the blades).

olivier's avatar
231
olivier
asked 2016-02-14 23:57:34 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2017-03-09 02:21:01 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

5

Since your fan doesn't bring air from outdoors, or an other zone, it's effect may be limited to two things: - the fan's motor adds some internal thermal gain - air velocity is increased in the zone, which may be relevant if you examine comfort. By default, e+ uses constant 0.137 m/s for PMV/PPD, you may increase air velocity by creating your own Air Velocity Schedule in the IDF file if you care about comfort.

adambgnr's avatar
749
adambgnr
answered 2016-02-15 07:05:29 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2017-03-09 02:21:14 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks I'll try it out. Comfort was what I was going for.

olivier's avatar olivier (2016-02-15 16:40:36 -0500) edit